Thread: Anchoring a Lathe to a Slab

  1. #1
    Join Date
    Feb 2006
    Location
    California...unfortunately
    Posts
    716

    Anchoring a Lathe to a Slab

    Gents,

    I am finally getting around to setting-up the machines in the shop of our new pad. All is well, except for my Emco Super 11 lathe. While it is a little jewel of a machine, it is light, to the tune of 850 or so pounds. As such, it has a touch of the wobblies that you can feel when running it, which is unsat. So I've started entertaining the idea of anchoring it to my slab.

    One idea I've had is to make riser blocks out of aluminum, about 5 inches tall, drilled and tapped to accept a length of threaded rod. The rods would go through the holes in the base of the machine, with nuts/washers being used for leveling, much like conventional machinery leveling feet. The purpose of the riser blocks is to raise the lathe so as to be more comfortable whilst working away. My other lathe is set-up similarly and it makes a world of difference comfort wise during long sessions at the lathe.

    None of the above is new, but my thought was using a high-strength epoxy of some sort to anchor the riser to the slab, which I've never heard of anybody doing. This would, in effect, anchor the lathe to the slab.

    While I'm no Epoxiologist, it would seem that modern epoxies would be plenty stong for this application, especially considering the stress on the epoxy joint would be minimal. Further, my Emco has leveling bolts on the bed, i.e., I can adjust the bedways INDEPENDENT of the conventional leveling process. If the lathe stand was seriously askew, and conventional leveling would unduly stress the epoxy joint (think twisted lathe stand being torqued straight during the leveling process), I can mitigate this stress by using the leveling/adjustment capabilities of the bedways.

    Another option would be to pour the riser blocks out of concrete and epoxy them to the slab, if this would result in a stronger bond.

    So what say you guys? If feasible, do you have any epoxy recommendations?

    Thanks for your replies,
    Justin

  2. #2
    Join Date
    Feb 2003
    Location
    Mt Pleasant Michigan
    Posts
    430
    They make epoxy for anchor bolts in concrete. I believe they have it at Home depot.

    Joe

  3. #3
    Join Date
    Dec 2003
    Location
    washington.........STATE that is.
    Posts
    11,033
    I AM an epoxiologist and will state as absolute fact that you cannot epoxy that thing down to the slab. Well, not and get it to "stick."

    Were it me (and I know IT AIN'T!) I'd consider bolting it down onto hockey pucks

  4. #4
    Join Date
    Jan 2015
    Location
    Greenwood, Ca
    Posts
    215
    Quote Originally Posted by alinwa View Post
    I AM an epoxiologist and will state as absolute fact that you cannot epoxy that thing down to the slab. Well, not and get it to "stick."
    In my yute, when in urban environments, we used to take left over Hilti epoxy (something like HY200?) and glue quarter to sidewalks for entertainment....

    I’d bet there’s still several odd epoxied rock formations on mountain tops all over CA and NV...

  5. #5
    Join Date
    Feb 2004
    Location
    Williamson County, Texas
    Posts
    296
    Lifted this from Long Rifles Inc. This is one epoxy application I would have bet not to last.

    "We also offer a machined/welded stand for our vise. The floor plate can be bolted or epoxied* to the floor.

    *LRI relocated to its current facility in 2011. The barreling dept stand was glued to the floor using JB weld. It has never failed. This was done because our shop has radiant floor heat and the risk of accidentally cutting the tubing matrix embedded in the concrete was just something we weren't willing to gamble on.

    Simply grind the floor clean with an abrasive pad (36 grit), remove the powder coating from the bottom side of the floor plate. Tape off the plate's footprint. Mix JB Weld and spread an even layer approximately 1/32" thick. Place the stand inside the square, peel the tape, and let it rest for a full 48 hours. (if the floor is cold, you may want to wait an extra day) Assuming all mating surfaces are sterile, you can work with confidence once the resin is cured. Should the stand ever need to be used, a rosebud torch can be applied to the base to warm it up and break the bond. Know that this will almost certainly ruin the powder-coat finish so its best to plan well ahead when deciding on placement."

  6. #6
    Join Date
    Dec 2003
    Location
    washington.........STATE that is.
    Posts
    11,033
    Single-point non-working loads with large surface area will rarely fail.

    You can weld an 8" square flange onto a 4" steel post and either bend the post or rip up a hunk out of the floor. I can't imagine a vise stand, grinder/buffer/worktable failing.

  7. #7
    Join Date
    Feb 2003
    Location
    Fbks,Alaska
    Posts
    342
    Quote Originally Posted by NezRongero View Post
    Lifted this from Long Rifles Inc. This is one epoxy application I would have bet not to last.

    "We also offer a machined/welded stand for our vise. The floor plate can be bolted or epoxied* to the floor.

    *LRI relocated to its current facility in 2011. The barreling dept stand was glued to the floor using JB weld. It has never failed. This was done because our shop has radiant floor heat and the risk of accidentally cutting the tubing matrix embedded in the concrete was just something we weren't willing to gamble on.

    Simply grind the floor clean with an abrasive pad (36 grit), remove the powder coating from the bottom side of the floor plate. Tape off the plate's footprint. Mix JB Weld and spread an even layer approximately 1/32" thick. Place the stand inside the square, peel the tape, and let it rest for a full 48 hours. (if the floor is cold, you may want to wait an extra day) Assuming all mating surfaces are sterile, you can work with confidence once the resin is cured. Should the stand ever need to be used, a rosebud torch can be applied to the base to warm it up and break the bond. Know that this will almost certainly ruin the powder-coat finish so its best to plan well ahead when deciding on placement."

    If the contractor was smart enough to bed the radiant slab "wersbo" tubing in sand under the slab rather than in the concrete,anchoring issues would not exist.

  8. #8
    Join Date
    Feb 2003
    Location
    VA
    Posts
    972
    If you are OK with casting concrete rider blocks, I would epoxy rebar into the slab at the block locations, roughen the concrete surface where the blocks would go, then use a bonding agent on the slab when you place the concrete. Structural engineers accept properly epoxied anchor bolts and/or rebar all the time. The key is "properly", making sure all the dust is cleared from the drilled hole. There are pretty good bonding agents used when placing concrete toppings on slabs. I wouldn't rely soley on a bonding agent, the epoxied rebar would keep it where it needs to be.

    Edit:
    Let me add, the weight of a lathe should keep riser blocks in place. I raised mine 5" with cast blocks, set in place, and they haven't moved in 10 years I think. If I recall, Mr. Tooley had pieces of steel rounds (4 or 5 inch) cut to place under his lathe, I don't think he anchored those.
    Last edited by Wayne Shaw; 04-26-2020 at 07:15 AM.

  9. #9
    Join Date
    Feb 2003
    Location
    CA
    Posts
    763
    Wedge Anchors might be part of the answer.

    Build your risers to length.

    Wield a flange onto each riser.

    The flange will be used to bolt risers to concrete slab via the Wedge Anchors.

    I would bolt the risers with flanges to the lathe, then drill the holes into the concrete, using the flange holes as a guide.

    If you ever want move the lathe unbolt it and cut and grind the bolts flush with the floor.

    Anyone ever use motor mounts for this type of application?

  10. #10
    Join Date
    Dec 2003
    Location
    washington.........STATE that is.
    Posts
    11,033
    I pour, mend and patch concrete for a living > www.sierraconcretefoundations.com < and agree with all the methods listed.... except just gluing her down.

    My issues with only gluing the lathe and block are that the lathe, under temperature variations grows and shrinks in length, and while the concrete floor expands/contracts at very nearly the same rate (ie, similar expansion coefficient) it's driven by a different set of variables. In other words, the lathe and the concrete floor are both 'alive' but not part of the same unit, and that epoxy under a working/vibratory load will fatigue/fail.

    Epoxied joints hate flex/vibration



    edited to add, link does not work..... don't know why
    Last edited by alinwa; 04-27-2020 at 02:22 PM.

  11. #11
    Join Date
    Dec 2003
    Location
    washington.........STATE that is.
    Posts
    11,033
    We're in the office trying to get the linkies fixed, not that it matters for this thread but this is a test

    http://sierraconcretefoundations.com/

  12. #12
    Join Date
    Feb 2003
    Location
    Tennessee
    Posts
    6,510
    Your pad will constantly move, let the lathe float on its own/IE leave the anchor bolts loose.

    NEVER bolt a machine tool tight yo a pad.


    ,

  13. #13
    Join Date
    Feb 2003
    Location
    Poetry, Tex.
    Posts
    6,669
    Quote Originally Posted by JerrySharrett View Post
    Your pad will constantly move, let the lathe float on its own/IE leave the anchor bolts loose.

    NEVER bolt a machine tool tight yo a pad.


    ,


    I agree.

  14. #14
    Join Date
    Jul 2005
    Posts
    571
    Quote Originally Posted by JerrySharrett View Post
    Your pad will constantly move, let the lathe float on its own/IE leave the anchor bolts loose.

    NEVER bolt a machine tool tight yo a pad.


    ,
    Works fine if the pad is large enough.
    The concrete pad under our largest lathes was five feet thick.
    It had lathes as large as 40 feet used to turn casting up to
    around six feet in diameter.
    I have a basement pad that is around 8 inches thick.
    It does not have ANY cracks in it.
    The 14 x 48 lathe bolted to it is not moving any time soon.

    I generally prefer to use epoxy secured threaded inserts and
    them level everything at the top of the mounting bases.

    The bases are used to hold the inserts in position during curing of the epoxy.
    When fully cured tighten the nuts up.

    Final leveling and alignment is between the drip pan and lathe feet.
    The Starrett 12 inch Machinist Level is very sensitive.
    You would swear the glass tube is an almost perfect cylinder.
    It moves plenty with 0.0010 inch shim under one end.
    Rated at 0.005 in per foot.
    Last edited by brickeyee; 04-29-2020 at 01:06 PM.

  15. #15
    Join Date
    Dec 2003
    Location
    washington.........STATE that is.
    Posts
    11,033
    so there Jerry!